Hi,
There is an strange problem with my DAQ board 6070E. When I am to use the pulse train of ctr0 as the source for DAQ Timing, I can not see the ctr0! I mean that from the list of sources to choose for DAQ Timing, I can see PFIs, PXI_Trigs, sample clocks and etc but there is no option for Dev1/ctr output.
Is there something wrong with my DAQ Board, or I am using wrong method to use a pulse train as the source of Timing?
Best,
Hosa
03-19-2012 06:40 AM
Dev1/ctr0 output connected to one of the PFI output, check device pinouts to define which PFI is "Dev1/ctr0 output"
Find your devise on Measurment and automotisation, right click on devise then => select device pinouts option
--
Regards,
Alexander
03-19-2012 02:07 PM
Dear Alex,
I did what you said. But none of both ctr outputs are on PFI. Only the ctr source and gate are on PFIs.
Best
03-19-2012 02:38 PM
Hi,
your card has AI START input on PFI-0, check board manual and find pinout for this input, then connect it with counter output on your screw terminal or connector block,
Use PFI-0 for start sync!
--
A.
03-21-2012 11:52 AM
Hi Alex,
It worked, Thanks for your suggestion. But, there is something that I need to ask you. I wanted to repeat the sample provided by NI with my DAQ Board 6070E. Please see here: http://zone.ni.com/devzone/cda/tut/p/id/4322 figure 3. The sample is a general sample for using pulse trains for synchronization. But When I check it, the sampling runs once and contunues no more. Can you help me on that?
Best,
Hosa
03-22-2012 05:11 AM
Hi,
last post i recommend you to use PFI-0, but it will be better to use PFI-1 as external timebase, PFI-0 generally used for start sync, but it doesn't matter. PFI-1 will work a bit faster.
I recommend you to use standard DAQ assistant for measurments, this function very easy to use:
Functions >> Measurment I/O >> NI DAQmx >> DAQ Assistant
Labview will ask you for measurment type, device ID, channels, etc. Select Voltage, your device ID and channel ID,
After that configure Assistant: Aquisition mode = continuous samples,
Same screen: select Advanced timing => Sample clock type = external, source = PFI-1 (or PFI-0)
Press OK, labview will promt a question to you: Confirm auto loop creation, press ok
I post example in attach
--
Regards, Alexander
03-22-2012 12:42 PM
Hi Hosa,
This bit of code should do what you are looking to do. You can use /DeviceName/CtrXInternalOutput as the terminal name for the sample clock of you AI task. CtrXInternalOutput is an advanced terminal, which you can enable for controls and constants by following this KnowledgeBase:
KB 3G0G2IZH: Enabling the Advanced Channels on a DAQmx Terminal Control/Constant
I've also attached the LabVIEW VI.
03-22-2012 02:05 PM
Thanks to Alex and Steven,
Both of your examples worked great as expected. There is one thing remained about the usage of pulse train. I mean, after successful generation of a pulse train, how to tell the DAQmx Read.vi to acquire more than one sample at each clock cycle? That is, for now the DAQ acquires only one sample at each clock cycle during the duty cyle. So, for example, if I want to get 100 samples at each duty cycle, how can I do that?
Best,
Hosa
03-23-2012 01:50 AM
Hi,
If I understand correctly, you want to aquire voltage signal at a frequency rate of 100 times greater than the timer output?
I dont think it is possible, you need timebase with same frequency rate.
03-23-2012 11:41 AM
As an example, for a counter with rate 1 Hz and duty cycle 0.5, it comes that the high part of clock takes half a second and low part of clock does the same. So, if I want to take more than one sample at the time clock is at high level, how can I do that? This is needed for averaging the samples at each clock pulse.
The other thing that comes in mind is that, am I going in right direction or not? I mean for the application I am considering, is this correct to use a pulse train as the clock or I just need a triggering plan to do the same application?
Thanks,
Hosa