I would like to use DasyLab with Siemens PLC Simatic S7-300. Which OPC Server shall I use?
I would like a manual for connecting DasyLab via OPC server to the PLC if it is possible.
Could I use NI OPC Servers which are compatible with LabView?
Thank you for your help
07-08-2014 07:30 AM
I believe that Siemens has an OPC server that you can purchase.
KepWare has the KepServer and drivers for Siemens www.kepware.com.
DASYLab has the Help menu with the instructions for the OPC DA modules. It's straightforward - configure the OPC server with the necessary drivers and connections (tags). Update rates are in milliseconds, for example, 100 ms is typical. You need to know your device and driver, to determine data types.
Once configured, KepServer has an OPC quick client to allow you to test your settings.
Then, add the OPC DA module to DASYLab, connect to the server, and select the tags to read or write.
Note that it's simple to set up on a single computer - to set up on multiple computers requires assistance from your It team to correctly configure the DCOM permissions. That's specific to the OPC server.
07-08-2014 07:31 AM
Yes, you can use NI LabVIEW OPC Servers... DASYLab will give you a list of available servers when you configure the connection.
07-08-2014 08:34 AM
thank you very match for your help
It was valuable