Hi,
I have a fault relay, where one side is tied directly to 24VDC.
The other side goes to a switch, ultimately to ground.
When the switch closes, the relay energizes and stays energized via a latching circuit.
The switch on the first line is a fault sensor which is normally open.
The switch on the second line is the latch, which is normally closed.
The third line is the DAQ input
24VDC --- RELAY --- SWITCH -------------- GROUND
|--- CONTACT --- SWITCH --- GROUND
|--- DAQ --- 2.4K --- GROUND
My problem is that I want to monitor the fault bus. I've tied the switched side of the fault relay to a 6514 DAQ input via an SCB-100. This works, and when the line goes low, the DAQ senses the fault. However, the internal circuit of the DAQ input has a 2.4K resistor which is a low enough value to keep my relay energized. I can't reset my fault.
Incidentally, the circuit I am monitoring is on a machine which has run for years. It's the introduction of my connection that is affecting this. Without the DAQ connection (remove third line from above circuit), I can reset the line and everything works fine.
Can anyone tell me how I can put something in between the external circuit and the DAQ input, such that I can sense the signal but not affect it?
Thanks,
Steve