Digital I/O
Digital modules for detecting 0-8VDC as OFF and 16-24 VDC as ON
Hello I am looking for I/O modules that can detect 0-8VDC as OFF and 16-24VDC as ON.
I went through the specs of the digital I/O modules on NI website. Everything that I saw had a range of 0-5VDC for OFF and 10-30VDC as ON. I would appreciate if anyone knows of NI digital I/O modules that have the specs I need. Otherwise should I go with an analog I/O module and process the "voltage" to ON/OFF in the program?
(3,719 Views)
Is the NI 9422 an option for you ?
(3,693 Views)
Thank you for your response. I did check NI 9422. The voltage ranges are 0-5VDC and 11-60 VDC. It does not match our requirements of 0-8VDC and >16VDC.
(3,688 Views)
Not NI, but you may want to contact Trenz regarding this module:
http://www.trenz-electronic.de/products/digital-io/te0102-td16i24.html
-AK2DM
(3,682 Views)
Hi Madhav,
Unfortunately we do not have any devices that support those input voltage levels for ON/OFF. However, if you are interested, you could use external circuitry to force the voltage to meet the specs of the DIO cards. A possible solution would be using a Schmitt trigger, but this is not support by National Instruments.
You could also use an analog I/O device, but keep in mind that you would be operating at slower rates as the logic levels would be handled through software.
Rohan B
(3,667 Views)