Hello,
Can you view the function blocks in Configurator? Is there any error message during device detection or function block access?
Please try the following step to set network parameters.
In Configurator, double click the link icon (interfaceN-N); In Network Parameters dialog, select Linking Settings(Advanced);Click "Press to see Suggested Values" to reset network parameters.
05-09-2008 05:38 AM
Hello Vince,
Thanks for the reply.
I can see the function blocks (partial) contained in the device (before defaulting the Network parameters); but I cannot use any of the contained function blocks to create a schedule because the entire parameters of the contained function blocks are not visible in the NI Configurator.
Defaulting the network parameters also didnt give a detailed view of the contained function blocks.
Does the NI configurator pickup the DD information from multiple local paths OR does it refer only the information contained under "\National Instruments\NI-FBUS\Data" folder ?
Regards,
Manish Gajjaria
05-11-2008 08:51 PM
Hello Manish,
NI-FBUS Configurator obtains DD information only from Data folder.
Which version of Configurator are you using on other PCs(PC 2, 3, 4...). Is it the same as the Configurator on PC1?
In Data folder of other PCs, please check the nifb.dct/nifb.ffo/nifb.sym files and make sure they are the same as the ones on PC1.
You can also try copying entire Data folder of PC1 to other PCs.
Regards