FOUNDATION Fieldbus

cancel
Showing results for 
Search instead for 
Did you mean: 

Unable to download simple PID loop configuration.

We have Foundation Fieldbus demonstration setup with Yokogawa's Flow meter , Positioner and Valve.
NI-FBUS configurator Ver 3.2 is used. We are  trying to set up simple PID loop with AI & PID blocks of Flow meter & AO block of Positioner.
We are unable to download the configuration.The error messages are

ERROR-NIFCONF-ERR-CONFIGURATION FAILED,Error Code - 1057
ERROR-NIF-ERR-MULTIPLE,ERROR code -3
 
Kindly provide solutions to the above problem
 
Regards,
Bhagyashree
 

 
0 Kudos
Message 1 of 3
(7,067 Views)
The error ERROR-NIF-ERR-MULTIPLE indicates that there exists duplicated block tags in the configurator. Please check the block tags in your PID loop configuration, make sure that there are no duplicated tag names.
Feilian (Vince) Shen
0 Kudos
Message 2 of 3
(7,053 Views)
 

Thank you.
We are able to download configuration after changing the tagname.
 
Best regards,
Bhagyashree