AI-110 incorrect readings

I'm getting incorrect readings in MAX from cFP-AI110 even when I wire 10Vdc directly to the input.  Does someone know what causes this to occur?
0 Kudos
Message 1 of 4
(3,506 Views)
rmorais,

What kind of readings are you getting? Do you have the module configured for -10.4 to 10.4 Volts? Have you double checked your supply voltage with a DMM or some other device capable of measuring voltages? Finally, do you see this incorrect reading on only one channel, or all the channels? Please let us know the details of the error and I'd be more than happy to help.

Regards,
Ryan Verret
Product Marketing Engineer
Signal Generators
National Instruments
0 Kudos
Message 2 of 4
(3,485 Views)
The AI-110 was picking up voltage readings from a load cell. All channels had the same problem, but it seems that it was the AI-110 card that was malfunctioning! I've switched to another one and that solved the problem!
 
Thanks for your interest!
0 Kudos
Message 3 of 4
(3,481 Views)
rmorais,

Glad to hear you found a solution! Please call 1-800-IEEE-488 if you would like to RMA this module.

Regards,