Hi, got a problem with the AO-200, it is connected with the FP1000 Network Interface that is connected to the 24VDC power supply, I connect the terminals V and C of the power supply to both modules. I'm using the channels 0 and 1, so I connect the wires in the terminals 1, 3 (+) and 2, 4 (-) and those are used to control a Samson PID and a Frequency Variator, and those are well connected to their respective analog inputs. When running the Test. iak, with the 3.5 - 21 mA attribute, the red leds of the channels 2-7 turn red and the 0 and 1 remain shut. The I run the LabView AO-200 VI and a mistake appears saying that the outputs are out of range: FP Write. In other tests I've connected the wires to a resistor (100 ohm) and a VOM in series but nothing runs through it and the same mistakes comes to the screen. I really don't know if I'm doing something wrong, but I guess so, because we own a couple of AO-200 modules and both don't work, so malfunction for both is a little bizarre, on the other hand, in other project I have an AO-210 working just fine and is wired just the same so I don't know if they are supposed to be wired differently or what........ Got help? Thanks.
0 Kudos
Message 1 of 2
(3,167 Views)
Chandus,

The Out of Range error indicates that the value you are writing to the channel is not valid. With the channels set to 3.5 - 21 mA, in LabVIEW, with the localized decimal set to ".", you would need to write a value of 0.005 for 5 mA.

For wiring mistakes on the [c]FP-AO-200, you will more commonly see the error "Open Current Loop".

Regards,
Aaron
LabVIEW Champion, CLA, CPI
0 Kudos
Message 2 of 2
(3,165 Views)