Can I apply a 24 VAC signal to a FP-DI-DC module?

I am monitoring 24 VAC actuated valves and cannot figure out which discrete input module to use. The threshold voltage on the FP-DI-AC120 is to high to respond to them.
0 Kudos
Message 1 of 3
(3,341 Views)
The FP-DI-330 will work with 24 VAC signals.

Regards,
Aaron
LabVIEW Champion, CLA, CPI
0 Kudos
Message 2 of 3
(3,341 Views)
Yes thank you. I have a number of FP-DI-330 modules already but I do not have the space to use one in this application. I only really need one discrete input. That is why I would like to use a dual channel module.