05-20-2010 07:26 AM
05-20-2010 04:56 PM
JB1,
"Configure Range.vi" will let you programmatically change channel ranges. I'm pretty sure you'll be using predefined ranges like +/-10v and +/-5v Available ranges should be listed in the manual for the FP-AI-100.
05-21-2010 01:36 AM
Thanks for the response but....
Perhaps I should have mentioned this when I asked the question but my fieldpoint units are connected using RS485 and configure range.vi is on the Ethernet pallet.
I am assuming that I need to do this using the optomux vis but, which one and how I know not and as yet have been unable to any of the optomux vis to talk to my fieldpoint devices at all.
05-25-2010 09:20 AM - edited 05-25-2010 09:21 AM
Hi JB1,
As stated in the user manual for the FP-AI-100 can only be configured for: 0–1 V, 0–5 V, 0–15 V, 0–30 V, ±1 V, ±5 V,
±15 V, ±30 V, 0–20 mA, 4–20 mA, and ±20 mA. So it won't be possible to work between -1.5 - 1.5 V.
Kind regards,
05-25-2010 09:30 AM
Hi Ben
What I really need to know is how to change the range programmatically. It doesn't matter what the range is.
Regards
JB1
05-25-2010 09:55 AM
Hi JB1,
Have you looked through the FieldPoint Optomux Programming Reference Help ? If you refer to the section "Attributes, Ranges, and Commands" this should help you change the range.
Regards,