Pete,
Every FieldPoint I/O module has an isolated I/O stage. This means that the common of the I/O module is isolated from the common of the backplane (which is the common of the network module). FieldPoint modules are rated for a working isolation voltage of 250 Vrms. This means that if you earth ground the network module (e.g. a common of 0 volts), you can connect the common of a FP-DI-301 to a value of 200 Volts, and be able to measure signals that range from 200 to 230 Volts with respect to the earth common. If you "cascade" wire the modules (e.g. wiring the V & C terminals of one module to the next) you bypass the isolation between those modules. If you cascade the network module, you totally bypass all isolation.
For further information, please loo
k at the following KnowledgeBase Article:
http://digital.ni.com/public.nsf/3efedde4322fef19862567740067f3cc/597c2b4cecef6bb586256831005b913f?OpenDocument
Regards,
Aaron
LabVIEW Champion, CLA, CPI