FieldPoint Family
Does cFP-TC120-8channels need PIN 20 of BackPlane?
I have broken the PIN Number 20 of Slot1 of the the BackPlane, but the cFP-TC120-8 works fine in that slot.
Could there be any impact?
Thank you.
(6,817 Views)
I am going to look into this and post an answer for you soon.
(6,803 Views)
Any ideas?!
(6,782 Views)
Accepted by topic author nikosfs
The first line on page 4 of the manual for this device states "The COM terminals of all the channels are internally connected and are connected to the terminals labeled C on the terminal base."  Therefore, the cFP-TC120-8 will work fine in that slot with #20 missing.  You can use any of the other COM pins or the C terminal connection in the terminal block (there are two of them). Pin #20 is COM (ground) for channel 1.
FP-TC-120 and cFP-TC-120 Operating Instructions
http://www.ni.com/pdf/manuals/373344a.pdf
(6,772 Views)
Thank you Patricia!
(6,767 Views)