What type of thermocouples are you using? How are they mounted? The [c]FP-TC-120 modules are not designed for a large amount of channel to channel common mode voltage. If several channels are biased with more common mode voltage than the others, you may observe this type of behavior. One solution is to re-arrange the thermocouples so that thermocouples that are at the same potential are on the same module. Also, make sure that you do not wire the V & C terminals from one FP-TC-120 to the next.
Regards,
Aaron
LabVIEW Champion, CLA, CPI