Rainer,
The FieldPoint IAK File is used in application programs (e.g. LabVIEW, LabWindows/CVI, OPC) for channel names, handle information and scaling information. FP Open.vi launches the FieldPoint Server with the specified IAK file, and uses the information in the specified IAK file for scaling (serial modules require scaling on the computer, ethernet modules scale the data in the network module) but does not re-configure the IO modules according to the IAK file. Likewise, opening an IAK file in FieldPoint Explorer does not reconfigure the IO modules to match the IAK file. The only times that settings are synchronized between the IAK and the modules are when a)the Find Devices command is issued (config from modules loaded), b) the Channel Configuration wi
ndow is opened (file or module config can be choosen) or c) a Snapshot command is issued (current settings of modules are stored).
Currently, the FieldPoint Server VI's do not allow dynamic re-configuration of ranges. If you wish to dynamically reconfigure your module ranges, you will need to use the FieldPoint Optomux VI's, which are located under the RT sub-palette of FieldPoint. They are installed by default only if you have LabVIEW RT, so you may need to re-install FieldPoint Explorer (custom install) to get them. For more information on the Optomux commands, please see the FP-1000/1001 Programmers Reference Manual.
Regards,
Aaron
LabVIEW Champion, CLA, CPI