The only way to configure an iak file is in MAX. And you must configure network watchdogs in MAX. You can configure module watchdogs in an RT FieldPoint controller; however, they are implemented differently and have more to do with making sure values are in their proper ranges.
You can try to get a newer version of MAX by downloading the latest version of NI-DAQ. I believe the version of MAX with this driver is 3.1.1.3004. However, this version of MAX has not renamed the button to the suggested "write to non-volatile memory on FP device".
05-31-2005 09:15 PM - edited 05-31-2005 09:15 PM
Message Edited by Aaron G on 05-31-2005 09:16 PM
11-11-2005 01:59 PM
I believe that I have found the source of the confusion regarding the WatchDog Timer (WDT) on the FP-1000.
I setup the WDT in MAX using Aaron's Method 1. The Bank Configuration was [Current - Enabled, 5000 ms / Power-up - Disabled, 0 ms]. I applied the settings (did not touch Snapshot!), exited MAX, and then ran my LabVIEW v6.1 application. I created the WDT situation (stopped the application with the machine running) and the WDT shut down the machine after 5 seconds. I then did a power reset on the FP-1000 and recreated the WDT situtation, but there was no shut down after 5 seconds.
Upon re-entering MAX, I was warned that the file and device settings didn' t match.
File settings: Bank Configuration was [Current - Enabled, 5000 ms / Power-up - Disabled, 0 ms]
Device settings: Bank Configuration was [Current - Disabled, 0 ms / Power-up - Disabled, 0 ms]
Just for fun, I set the Bank Configuration to [Current - Enabled, 3000 ms / Power-up - Enabled, 5000 ms ], applied the settings, exited MAX, ran my application, and created the WDT situation. The WDT stopped the machine after 3 seconds. I then reset the power on the FP-1000 and recreated the WDT situation. The WDT stopped the machine after 5 seconds. I cycled the power again and got the same result, the WDT stopped the machine after 5 seconds.
Upon re-entering MAX, I was warned that the file and device settings again didn' t match.
File settings: Bank Configuration was [Current - Enabled, 3000 ms / Power-up - Enabled, 5000 ms ]
Device settings: Bank Configuration was [Current - Enabled, 5000 ms / Power-up - Disabled, 0 ms]
So, the FP-1000 runs with the applied settings until a power reset, then it operates with the Power-up values shifted to the Current fields and the Power-up fields zeroed. I found the same behavior with both FieldPoint v4.0.1 and v4.1 drivers. However, I wasn't able to run my application with the v4.1 drivers. I observed the shifting of the Power-up values to Current, etc. via MAX. My application failed with v4.1 because it couldn't find a FieldPoint Server .dll (no name - just ".dll") and so the FP.Open.vi failed to run. Not sure what's going on there, I told FieldPoint on installation to skip the LabVIEW v7.x support but to install the v6.1 support - it acts like it ignored my command, installed v7.x and skipped v6.1 (or perhaps installed neither one?).