Hi Mir. I don't know of a way to monitor the modules themselves, but the Error Out terminal
on the FP Read.vi will tell you if there is a detectable error (open RTD or TC, etc.) on an input
channel. Should be fairly simple to read both of your FieldPoint units then parse through the
results for channels without errors.
Note that if you use the 'read all' instance, the error returned won't be specific to a channel but
rather will indicate error or no error for the module.
Maybe buffer several readings and then look for an appropriate minimum amount of noise to
try to catch a module returning the same value all the time (I haven't seen this, just thinking out
loud about detectable things that might happen).
Matt