There are several items in the tag configuration that you should check as they may cause extremely slow updates. First (and most likely), check the Update Deadband. If I recall correctly, it defaults to 1%. With an FP-TC-120 set to -270 to 1770 C, that is 1% of 2040 C or 20.4 C. This means that the engine will automatically filter out changes that are less than 20.4 C from the initial value. Next, check the tag update rate. You should set it for an interval of 1.13 seconds (All Channel Update Rate of the FP-TC-120). Finally, check the group update rate.
Edit: A more appropriate deadband would be 0.05% or 1.02 C with the -270 to 1770 C range.
Regards,
Aaron
Message Edited by Aaron G on 03-06-2005 08:38 AM
LabVIEW Champion, CLA, CPI