Ben,
1) The FieldPoint and Compact FieldPoint lines are tested according to CE and other standards for EMC/EMI vulnerability. For more information, refer to the Declarations of Conformity for each product (available online at ni.com->support->Product Reference->Product Certification->Distributed IO). The D.O.C.'s may specify mounting or shielding conditions required for a product.
2)The input circuitry on the [c]FP-AI-102 modules uses a calibrated resistor divider network (1 Meg Ohm input impedance per channel) on each channel. With the maximum measurable input of 120 Volts, the total expected current flow through a channel is 120 uA. With the 1 Meg Ohm input impedance, each volt of input provides 1 uA of current flow through the input resistor circuitry.
3) All channels of the [c]FP-AI-102 share a common "ground" within the IO module (user accessible via the Com and C terminals). The common for each IO module's inputs is actually isolated from the backplane/terminal base ground (network module C terminals) and can float (within the published specifications) at a different potential from the backplane/terminal base ground. This isolation of commons from module to module will be bypassed if you have wire the C or Com terminals from one terminal base to the C or Com terminal of a different terminal base. Thus, there is the possibility for ground loops to occur if the transducer "grounds" for two different modules are at different levels and the modules have the C or Com terminals tied together. (Side note: some people wire the V/Vsup and C/Com terminals of multiple modules together to share a single power supply, however, many input modules and some output modules do not require external power, so this is unneccessary).
It sounds like you have already localized the problem to certain wires and physical locations for EMC purposes. Depending upon the nature of your current wiring solution, you may want to try either twisted pair or shielded cables in the problem area. Additionally, you can also check the grounding of the chargers within the affected area.
Regards,
Aaron
LabVIEW Champion, CLA, CPI