Mike,
Error code 33162, "Can not connect to item on module," generally is the result of attempting to connect to an item that is not available at the first connection attempt. This is frequently the result of an ethernet network module being offline when you attempt to connect to it. Since you are able to connect from FieldPoint Explorer, I suspect something else is going on. The likeliest possibilities that I can think of are:
1) You have more than one ethernet Comm Resource in your IAK file and you have provided the name for the wrong resource (e.g. you may have had a different IP address and created a new Comm Resourcefor the new IP address, but left the old one in place and are using the wrong one).
2) Similar to #1 above, you changed the IP address in
the Comm Resource but did not save the change so there is no module at the IP address it is attempting to communicate with.
3) There is a misconfiguration in the IAK file and the FP-TB-10 shows a listing for a digital module at address 0 rather than an analog module.
4) The module is misaddressed. I have occasionally seen instances where the protective end cover was not installed on the last terminal base and a piece of metal shorted some of the pins causing the addressing to be incorrect. Since this method of failure would also show up in FieldPoint Explorer, I do not think it is likely the root cause of your problem.
5) You have booted the FP-20xx in Safe Mode (although FieldPoint Explorer will not work in this case so I do not think it is likely).
Note: If you had successfully connected and then lost the connection, the error code is 33163, "The connection to the module has been broken."
Regards,
Aaron
LabVIEW Champion, CLA, CPI