1. The @0 and @1 denote the location of the module in the bank. For example, the FP-2000 is at location 0 in the bank. This means it is the first module. The FP-TB-10 is at location 1, meaning it is the second module in the bank. Here is an example of the FP bank layout:
|@0 | @1 | @2 | @3 | @4 | @5 | @6 | @7 | @8 | @9 |
After clicking start monitoring, the icons turn blue. You can tell that you are communicating, by looking under the Status column. If you are not communicating, the status will say something like "Connection Broken".
2. In order for the FP Bank to detect your new AO-V10B module, you must right click on the FP Bank and select "Find Devices". This will cause your FP Bank to search for new devices. After you have done this, you can c
lick on the FP-TB-10 and you should see two of the channels as Analog Output.