Rainer,
1) You can do this using the Optomux VI's which are located at: ftp://ftp.ni.com/support/fieldpoint/LVFPOpto/
Please note, that after changing the range of a channel, you must wait for a period of time that is greater than or equal to the All Channel Update rate of the module prior to reading the channel that you just changed the range on. This is necessary to avoid scaling data acquired on the old range setting with the scale of the new range.
2) The configuration VI's are ethernet based and do not work with serial modules. Instead, you should use the FieldPoint Optomux VI's that I reference above. The FieldPoint Optomux VI's are instantiations of each of the commands in the FP-1000/1001 Programmers Reference Manual.
3) The FP-SG-140 is a ne
wer module and has not yet made it into the FP-1000/1001 Programmers Reference Manual. I will post the proper range/attribute/command settings for the module later today or early tomorrow.
Regards,
Aaron
LabVIEW Champion, CLA, CPI