Bob,
Because the program is set to start-up when the FieldPoint module starts, you must first disable the start-up of the VI. You can do this via the Disable switch or via LabVIEW RT. Because the VI is running, when you first connect to it with LabVIEW RT, you will need to stop the missing VI from the warning dialog box before completing the connection to the target. You can then un-select Tools>>RT Target Options>>Miscellaneous, Launch Code at Startup.
Next, reboot the controller. After the controller is rebooted, ftp to the module, switch to the directory \ni-rt\startup and rename the file from startup.exe to nomore.exe (nomore.exe can be any 8.3 compliant filename). You can then delete the renamed file from the controller. Close the ftp connection and you are done.
Regards,
Aaron
LabVIEW Champion, CLA, CPI