FieldPoint Family
How to connect to a output module that acts as a current sink with a common ground
I have a Simpson Power Meter, GIMA, with a Output Options Module.  The Module provides for 4-20 ma signal transmission up to 4 variables.  It acts as a current sink with a common ground; please see the Module schematic in the attachment.  Attempts to wire the signals to FP-AI-110 module have failed.  Initially, the 24 Vdc power from NI was used and the input was configured as a 4-20 ma input...this did not work.  Second attempt signal isolators were installed and the meter power supply was used to connect the signal to self-powered signal isolators from Crompton (250-ISAU-HG).  The isolator output had a 250 ohm resistor across it and the AI-110 was configured for a voltage input...but this wiring failed as well.  Advice on how to make this connection work would be deep welcomed and appreciated.
(3,708 Views)
gti,
As both modules are current sinks with common grounds I don't think you'll be able to configure the AI module for taking a current measurement.
You might however be able to hook these up to take a voltage measurement.
This KB explains how you would set this up for digital inputs:
How Do I Connect Two Sinking I/O or Two Sourcing I/O Together?
I think that by selecting an appropriate pull-up resistor and voltage source you will be able to take a voltage reading that reflects the current going into the AO module.
I hope this helps.
Simon H
(3,699 Views)
Simon, thanks for the reply.  The holidays have delayed further troubleshooting on our end.  We will review your advice and hopefully resolve the problem.  We have also sent a email to the electonic circuit designer who resides in England, the name is ND Meters, for assistance.  A little side note; one reason the Simpson meter was selected was that it was made in America, no offense to our global brothers.  We are definintely in a world economy.  Thanks again.
(3,646 Views)