Normally the cFP or FP controller has no probling giving access to a PC without it specifically being on the IP list. Despite adding the PC on the IP list, I still get the same error.
Søren h. jensen
‎12-11-2006 08:43 AM
‎02-15-2007 10:08 AM
‎03-12-2007 09:23 AM
‎03-14-2007 01:52 AM
I attempted to update these data with Measurement & Automation Explorer (MAX) using the "FieldPoint Access Control" panel in MAX: I set "*" and Read/Write and pressed "Apply": MAX Claims it has updated the Access Rightsm, but we are still unable to Deploy the CFP from the Project Explorer.
SOLUTION:
Use WS_FTP-PRO (or any FTP Client) and access the IP Address of the FieldPoint using anonymous login.
Transfer the file ni-rt.ini from the root of c:\ on the Fieldpoint to the local PC and edit the settings as shown below.
FTP the file back to the Fieldpoint.
Set the following settings in "server.tcp.access" and "RTTarget.IPAccess":
server.tcp.access=""+*""
NOTE: Double Quotes here
RTTarget.IPAccess="+*"
NOTE: Single Quotes here
+* means every IP address can access.
It turned out that MAX had left the following (probably illegal) values in the fields:
"""" and ""
‎03-20-2007 10:42 PM
Geir,
Nice fix. I've spent the last 3 hours reformatting my cFP drive, and reinstalling the software (multiple times) just to be able just to reconnect to the target. I wish I checked out this forum sooner.