I am in the process of adding a second, remote, FP1001-based node located
2000 feet away from my existing cFP2020-based node. Communication will be
via RS-485 over buried cat5e. Additionally, this second node will acquire 4-20mA
data from a two-wire pressure sensor located a third location 1000 feet further
away, loop-powered off of this fieldpoint's PS-4 power supply. All fieldpoints and
transducers are inside buildings.
I am concerned that I properly protect all fieldpoint hardware from lighining-induced
surges. To this end:
1) Both fieldpoint nodes' 120VAC power is fed through industrial surge protectors.
2) I plan to install appropriate industrial surge protection devices at both ends of the 2000 foot
RS-485 link between the fieldpoint unit
3) The two-wire 4-20mA link will also have industrial protection devices designed for 4-20ma loops
at both the fieldpoint end and at the transducer end (the connection will be made via one pair of
another buried cat5e line).
All protection devices will be robustly bypassed to the local ground.
Is this scheme adequate? Should I be independently powering the remote sensor? Any
additional recommendations or corrections? Lightning is a significant risk in this 7000-foot
Colorado location (Got a hit in my backyard yesterday).
If it matters, the planned protection devices are MTL ZoneBarrier devices.
Bob