Redundancy in fieldpoint

Hi is there redundancy possible with Compact field point system. if yes, what level we can get redundancy 1. I/O Level , 2. CPU Level, 3. Powersupply Level. Kindly let me know ASAP. I am at very urgent need to decide.

with regards

R.sathiyanarayanan
0 Kudos
Message 1 of 2
(3,487 Views)
Hello,

Thank you for contacting National Instruments.

There is built-in redundancy at some of the levels that you have mentioned.

1. At the I/O level there are built-in watch dogs that will set the lines to a default level if a system crash or error occurs.

2. At the CPU the watch dog timers will also help determine if the CPU has hung or encountered a problem and will react as you have configured them.

3. At the power supply level, you have the option of connecting, a second, backup power supply in parallel with your dedicated power supply. The network controller has multiple power connections that allow this to be done. Users commonly connect a battery to this backup power supply connector.

Regards,
Bill B
Application Engineer
National
Instruments
0 Kudos
Message 2 of 2
(3,487 Views)