Kerry,
There are several different things that may be going on here. First of all, there may be an issue with power consumption. A network module (FP-1000 in this case) is designed to source up to 9 Watts of power to I/O modules. This assumes an average of 1 Watt per module. Certain modules require more than 1 Watt, most require less leaving extra power for the ones that require more. In your configuration, you may be over this depending upon how your FP-TB-10's are populated. Assuming that the TB-10 is unpopulated, your consumption is 4 * 0.35 + 2 * .25 + 2 * 0.6 + 1.7. = 3.8 Watts. Thus, the load from the Dual Channel modules may not exceed 5.2 Watts. If you are using exclusively the Dual Channel Analog Out Current modules, you will overload the power supply.
Anothe
r thing to look at is when resetting the network module, check the box that says factory configuration. After the reset, uncheck the box and then configure your channels and power-up values (edit this device on each module).
Also, there are some times when relays may get "stuck" in an on position due to extremely high inductive loading. I have not seen that happen very frequently, but it does make me wonder, what type of load are you driving on the relay channels?
The PWM module, has 12 bit resolution, and will accept values of 0% for the output duty cycle. What value for the period have you set?
LabVIEW Champion, CLA, CPI