What can I do about error codes 33487 and 33443 from FieldPoint.

I am using the AI-111 current module with FP 1600 network module. I checked all wiring and connections and I can't find what is causing the problem.
0 Kudos
Message 1 of 5
(3,980 Views)
I did not find an explanation of the 33487 error.

Does the device work from FP explorer?

Ben
Retired Senior Automation Systems Architect with Data Science Automation LabVIEW Champion Knight of NI and Prepper LinkedIn Profile YouTube Channel
0 Kudos
Message 2 of 5
(3,980 Views)
Check out the FieldPoint Help files under the category of Errors and Warning Codes.

Error code 33487 indicates that the channel has returned an Out of Range warning. This will be returned by the FP-AI-111 if the channel measures a value that is outside of the configured range.

Error code 33443 reports that several contained channels reported a bad channel status. This would be returned when you are monitoring a multi-channel item and one or more channels reports an out of range error.

Since you are using a FieldPoint Ethernet module, you can have FieldPoint Explorer open while your program is running to see which channels are specifically going out of range. Remembering that the FP-AI-111 is a referenced single ended measurement module, it may be that yo
u have a ground loop causing one or more channels to appear to be out of range. Alternatively, you may have incorrectly configured the channels (for example, setting the range to 3.5 to 21 mA with a 0 to 20 mA device).

Regards,
Aaron
LabVIEW Champion, CLA, CPI
0 Kudos
Message 3 of 5
(3,980 Views)
Thanks Aaron.

I have checked each channel individually, making sure the wiring is correct and tight as the well as the range is set correctly since I am using 4-20 mA sensors. The only thing I found is that I am getting a reading on one of the channels when there is nothing connected to the spot on the terminal base. Also, I disconnected all the sensors an I am still getting a reading on that channel.
0 Kudos
Message 4 of 5
(3,980 Views)
Ruleo,

It is common to have a reading on a disconnected channel. Generally speaking for measurement devices, un-connected voltage inputs tend to float around to either the positive or negative supply rail of the measuring device and current inputs will float around the 0 mA range. This is due both to device design and the real world behavior of components as opposed to the ideal behavior model. Some devices such as the FP-TC-120, will have circuitry to cause un-connected outputs to go to a specific level (in the case of the FP-TC-120, unconnected outputs will always read full scale of the range).

When you say you are getting a reading on that channel, is it a reading that is close to mininum scale, or is it a reading in the middle of the
scale, i.e. 10.2 mA? If the channel is not reading close to minimum scale, it is possible that the channel has been damaged. On the FP-AI-111, you can use a DMM to measure between the Iin pin and any of the C or Com pins. First disconnect any external wiring to the channel, then hook in the DMM. The resistance (within the accuracy of the DMM) should be exactly 100 Ohms. If the resistance is greater than 100 Ohms, then the channel was damaged by an over-current condition that exceeded the published specifications of the module (30 mA). In that case, the module will have to be sent to National Instruments for repair.

Regards,
Aaron
LabVIEW Champion, CLA, CPI
0 Kudos
Message 5 of 5