FieldPoint Family
command set for cFP-1804 and cFP-TC-120
Before the FP modules were obsoleted, I was using them to collect thermocouple data via a serial connection to an Allen Bradley PLC, which integrated control and acquired data from the Fieldpoint. I switched to the cFP-1804 and cFP-TC-120, since the old system was no longer available, and despite the assurances from NI support that the command languages (and repeated requests for me to use various drivers that cannot be used in my application), the old code doesn't work at all. So... I need a command set reference for the cFP-1804 and cFP-TC-120 so I can write to the system, configure it, and ask for data. The old codes looked like: >01!f000F000110221000110221000110221000110221?? to configure the modules, e.g.
(6,126 Views)
Accepted by topic author stericert
stericert,
I'm sorry that you're having trouble.  You may be experiencing problems because the cFP-1804 supports only the extended commands and the Power Up Clear standard command.
For additional information on the extended commands, refer to the FieldPoint Optomux Programming Reference Help.  This is also the full command set reference you asked for.
http://digital.ni.com/manuals.nsf/websearch/A62558E5BDED8486862573460055DF12
Drew T.
Camber Ridge, LLC.
(6,117 Views)