FieldPoint Family
communication failure
Hi Yves,
please report me your results and tell me if i can help you.
best regards
Alexander
Message 11 of 18
(4,864 Views)
Hi
I don't get it.
The 33162 errors occurs quite randomly. But hardly ever they last for about 5 to 6 seconds.
Now I'm looking to monitor network traffic and cpu load.
Maybe...
Message 12 of 18
(4,845 Views)
Hi Yves,
can you post some code for me so i can look into it?
What are the results, how looks your network traffic?
best regards
Alexander
Message 13 of 18
(4,836 Views)
Hi Alex
Thank you very much for your support.
I might have found the error: In a small subvi I found a while loop running without any timer... (And because I load some vi's dynamically and reentrant there were more than one.)
In fact I would have expected  a rise of cpu load du to this but there was none.(Maybe due to the quite short time the while loop was running.)
Up to now I had no communication error for 8 hours.
Well I found it quite odd that the error message lead me to a communication failure...
Yves
Message 14 of 18
(4,828 Views)
Hmmm, thought I had the error. But I wasn't lucky.
I have set a  "Get/Time in seconds" in the acquisition loop. And I compare the elapsed time between every cycle.
And now I have seen that this loops isn't running fast enough from time to time. Sometimes it take more than 5 second!
Although I have set this loop on high priority.
How can I check where this problem comes from?
Yves
Message 15 of 18
(4,785 Views)
Hi Yves,
how looks the CPU in the task manager.
Can you please post some code so i can look into it?
How fast should the loop run?
Are you using Timed Loops on your windows system to get the values back from the cFP-1808?
best regards
Alexander
Message 16 of 18
(4,771 Views)
Accepted by topic author Yves
Hi Alex
I just wanted to thank you and all the others for having tried to solve my problem.
It sounds really incredible.
By great luck we found out what the problem was: Our lab consists of 10 "Fieldpoint-station". In one of those station was a water leak which drops on the 24VDC power supply for the FP-Controller. From time to time, of course.... Murphy
The water drops came from a pneumatic valve block right above the power supply.
Due to the water drops the power supply stopped and started again. And of course the FP-Controller had to start again to. Unfortunately this problem occured on various time and couldn't be tracked very easely.
Yves
Message 17 of 18
(4,310 Views)
Hi Yves,
thanks for this information i think that was realy Murpy 🙂
best regards
Alexander
Message 18 of 18
(4,295 Views)
