The FP-AI-110 module can not be used to measure an LVDT transducer. LVDT transducers require AC excitation and provide an AC output (see http://www.ni.com/sensors/lvdt.htm for basics of LVDT sensor operation). The FP-AI-110 module (and the FP-AI-100, FP-AI-102) are designed for DC voltage measurement, not AC as required for use with an LVDT. To my knowledge, the SCXI-1540 is the only National Instruments product directly designed for use with LVDT sensors. Alternatively, some companies make LVDT to DC voltage converters that could be used in between the FP-AI-110 and the LVDT.
Regards,
Aaron
LabVIEW Champion, CLA, CPI