FP-1000, FP-AI-100 all set up and communicating. Analog input has been monitored in FP Explorer. The .iak file C:\Temp\FP920 has been saved. Can close FPE then reopen C:\Temp|FP920 and again read Analog input. Configured an analog proram in LV. Did not work. Tried examples in LV for FP Temp. Get error 32800. Path for .iak file not there but it is. Wat's wrong??
Assuming that everything is confgiured exactly as it is written above, then the path in LabVIEW should be the following, without the quotes, "C:\Temp\FP920.iak".