Hardware Developers Community - NI sbRIO & SOM
Minimum Requirement for SOM9651
I have designed a board for SOM9651. At the moment I am trying to connect to the SOM module on the board. As it is the first startup of my board, I did only place a minimum configuration of components to get startet.
This includes:
- Ethernet0
- USB0
- 3.3V Supply of the module
- 3.3V Supply of Bank1
- 1.8V Supply of Bank2
- 3.3V Supply of Bank3
- Reset, Status LED and Temperature warning Pull UP for DIO35
- a few I/Os to be testet later on
The status LED of the module starts flashing, when the power is on. It does react on the reset button ... but it will keep on flashing when the reset button is released.
The discription of the status LED flashing in the "System on a module OEM Device" specifications is not very clear about this fault. Is the module damaged? Is the problem caused by a bad design? I have ordered two more modules, but I haven't received them so far.
so long, ...
(6,012 Views)
dear matt
I recommand check reset voltage. It might be a mistake to hold reset
voltage by mis circuit design. I also have a similar problems at my fisrt
test board.
Keep it touch your status.
2016년 2월 29일 월요일, Matt_McLaughlin<web.community@ni.com>님이 작성한 메시지:
NI Community <https://decibel.ni.com/content/index.jspa>
Minimum Requirement for SOM9651 reply from Matt_McLaughlin
<https://decibel.ni.com/content/people/Matt_McLaughlin> in *Hardware
Developers Community for NI Single-Board RIO and System on Module* - View
the full discussion <https://decibel.ni.com/content/message/130721#130721>
(5,671 Views)
I had a similar problem, custom carrier board, NI SOM blinked status lights, briefly responded to the reset button and went back to blinking. Never responded to pings, nothing on the serial-0 port.
Voltages were fine, I swapped it out with a different NI SOM and it worked perfectly. Apparently one of them in the batch we got was deffective or something. No problems since.
(5,671 Views)
Thank you for your response.
I had low voltage on the module supply about 3.1V
Now the module is working.
(5,671 Views)