Industrial Communications
PROFIBUS Master DP Error
I have a cRIO 9024 with a Comsoft PROFIBUS module in slot 1.  Following instructions provided, I am able to download the configuration.
However, the LED on the module are as follows:
PWR: Green
SPI: flashing green
RUN: Green
BF: Red
Looking at the manual, it tells me the possible reasons are a a configuration error or a non-responding DP-Slave.
I have attached a screenshot of my configuration, but I don't think I've made any mistakes, and the pumps are all configured to the bus addresses (3-14).  I've checked the cables and they are all connected (daisy-chained.)
What could be the source of this error?
-Larry
(6,899 Views)
try going online and see what happens.
Jesse Dennis
Engineer
INTP
(6,895 Views)
Hello Jesse,
Do you mean the Monitor/Modify connect button the the Configurator?  When I press it, all the slaves show up as red, and when I click on the property of one of them all the inputs/outputs show up as "fault."
(6,881 Views)
Hi Larry,
That is the correct button. The configurator isn't finding your slaves, I would check that they are online and configured correctly. Once they are configured correctly they will show up as green in the configurator.
Jesse Dennis
Engineer
INTP
(6,876 Views)
Jesse,
The PROFIBUS is connected to 7 Grundfos SMART Digital DDA metering pumps.  They should be connected, have power, and I have set their bus addresses to the ones corresponding to the configurator.
It shows a "Bus error" however on the pump.  Is there something aside from the bus address that I need to configure on the pumps themselves?
-Larry
(6,873 Views)
Jesse,
I managed to figure out the problem.  One of the cables was damaged.  I am now able to communicate with the pump through the examples provided by the Labview driver.
Now I am not sure how to utilize the inputs I receive in a meaningful way.  For example, I have one of the inputs set as the "ActualManualSetpoint."  I change the setpoint on the HMI of the pump itself, and there are 4 numbers that do change whe nI do this.  However, these 4 numbers don't correspond in any way I can see to what I am setting as the set-point.  Do you have any idea how I can convert these numbers to usable data?
The pumps are Grundfos Digital Dosing DDA.
Thank you for your time.
-Larry
(6,839 Views)