485 (GModbus) CRC/LRC error
    I am getting a CRC/LRC error from a half duplexed 485 system connected to a Watlow controller.  I have the instrument configured in MAX for 4-wire auto and I have this code running on other identicle systems with out an issue.  Does anyone have an idea as to what would cause such an error?
(4,242 Views)
Accepted by topic author teslac
In most cases I know a 485 connection is a 2 wire connection. Maybe you should set MAX to 2-wire auto.
Kees
(4,220 Views)
That would be good to try but unfortunatley MAX has that section greyed out and I cannot change it and am not sure how to get MAX to let me.  Do you know why MAX has that greyed out?
(4,215 Views)
I think it depends on the kind of interface you are using. Is it from NI or ?
(4,198 Views)
 It turns out that the reason for it being greyed out was to change the advanced functions you must logon to MAX as admistrater.  Once I had access I changed the 4-wire to 2-wire auto and the system worked fine.
(4,164 Views)
