09-14-2015 12:12 PM
I have to control 4 proportional valves (Bürkert 2873 x 3 & 2875 x 1) installed on a gas line. These valves control signal type is 4-20 mA. I have a NI USB-X 6343 daq with 4 AOs of -10 - 10 V. How can I control these valves with this daq device? I am not familiar to electrics/electronics, that's why I am asking. Thanks in advance.
Solved! Go to Solution.
09-14-2015 12:53 PM
That device can only output 5mA on the analog output. So you will need an op-amp that can output over your 20mA. See here for creating a converter circuit with an op-amp. Your USB-6343 should be supplying the 1 to 5V to the op-amp.
09-14-2015 02:29 PM
Thank you crossrulz. I checked the page that you suggested. Is this circuit is enough to create 4-20 mA signal? just with a resistor of 250 ohm, and a transistor?
09-14-2015 06:19 PM
I is not a transistor. It is an op-amp. It will need an external power source (5 to 10V should do).
09-15-2015 09:04 AM
09-16-2015 12:50 AM
Thank you AnalogKid2DigitalMan. They seem quite useful. ![]()