Reason for 4-20mA current as a standard signal for transmitting data to and from PLCs
What is the reason behind the 4-20mA current as a standard signal for transferring data? Well for starters, we choose current over voltage because there is less signal / data loss when the signal is being transferred over.
How about 4-20mA?
Well the purpose of having 4mA as a minimum is to be able to make sure that process actuators are "on" so that SCADA is able to detect any possible fault. Is that right?
how about 20mA?
(3,786 Views)
See http://www.control.com/thread/1026235722 for one discussion on the subject.
(3,779 Views)
I don't know if this is mentioned in the link Dennis provided.
With 4mA as a minimum you can detect an open loop. Actually the complete range is 0 - 24mA. The proces value is 4 - 20mA. Below 4mA is a open line and above 20mA is a shorted line.
Sometimes there are also value ranges like 3-4mA and 20-22mA as transmitter faults.
Kees
(3,770 Views)
you can build sensors that can be powered with the remaining 4mA so only two wires needed to get the signal and power the sensor
Greetings from Germany
Henrik
LV since v3.1