03-11-2013 08:54 PM
Hi,
What is the reason behind the 4-20mA current as a standard signal for transferring data? Well for starters, we choose current over voltage because there is less signal / data loss when the signal is being transferred over.
How about 4-20mA?
Well the purpose of having 4mA as a minimum is to be able to make sure that process actuators are "on" so that SCADA is able to detect any possible fault. Is that right?
how about 20mA?
03-11-2013 10:11 PM
03-12-2013 02:59 AM
Hi,
I don't know if this is mentioned in the link Dennis provided.
With 4mA as a minimum you can detect an open loop. Actually the complete range is 0 - 24mA. The proces value is 4 - 20mA. Below 4mA is a open line and above 20mA is a shorted line.
Sometimes there are also value ranges like 3-4mA and 20-22mA as transmitter faults.
Kees
03-12-2013 06:34 AM
you can build sensors that can be powered with the remaining 4mA so only two wires needed to get the signal and power the sensor