Hi RC007,
Thank you for the description of motor dithering, I had not heard of that before.
The NI-9485 has a closing time of 9mS, opening time of 0.5mS when used within the specifications listed as: -40 to 70 degrees Celsius.
If you have a lower current requirement or operate at a fixed temperature then the open/closing time will change as well.
The MTBF of this device is 2,172,740 hours as stated on page 14 of the
manual.
Here is more information, there is a chart where you spec the current and ambient temperature then read off the switching speed.
Please post back if you have more questions regarding this application.
Best regards,
MatthewW
Applications Engineer
National Instruments
Message Edited by Matthew W on 08-01-2007 03:28 PM
Message Edited by Matthew W on 08-01-2007 03:33 PM