9403 to control a relay (on/off heating)
I am building a temperature control system, I already have the PT100 measurement using the module 9205 (16bit analog input). For the controlling of the temperature:
I am using 300W heaters connected to 230V and the 9403 module , as well as SSR Crydom ED24D3R. I am trying to do this "phase fired controller" in Labview. But I do not know how to get it arranged so that the PWM starts together with the AC .
Am I right with this reasoning? I don´t have much experience in this.
Any other ideas how to control the temperature with the heater-relay set-up?
Thank you! 🙂
(2,641 Views)
Getting in sync with the line phase migth get tricky, your SSR doesn't seem to have a zero crossing detector .
Depending on the termal mass I would start with a first and easy try: a pulse packet control, say a slow PWM 🙂  with 10s (or 2s)  periode and 10 power steps.
300W isn't that much load, so flicker shouldn't be a problem.
If your system allow to measure a step response ( from a cold system, turn on the heater and measure the temperature until a limit is reached )
 this would help to design a controller.
If you really need a line phase sync you can use a small transformer and one analog in , or just a optocoupler (with some additional circuitry search the EDN design ideas for some hints) with a DI.
Using an SSR with zero detector will help.
Greetings from Germany
Henrik
LV since v3.1
(2,606 Views)