Connect sensor open collector output to NI USB-6
Good morning Labviewers,
I need to read a frequency (voltage pulse) signal with my NI USB-6229. I already have prepared a vi to do this, but now I'm struggling on how to connect the sensor to it.
My sensor is a Bukert flowmeter 8030 - SE30. The supply voltage needed is 24V and the output I'm using is NPN 0,2 - 36V, open collector.
To measure this signal, I'm using a DAQ NI USB-6229 which maximum input voltage is +10V.
I measured the voltage output (or what I think it's the output)  from the sensor and it was 22V, which I can't connect to the card directly.
I've read about using the +5V output from the same card to the open collector, but I'm not sure how to do it.
Can someone help me with this matter? I really need to test this asap.
Thanks in advance!
Vanessa
(3,551 Views)
Accepted by Vanessa86
The first half of this article might help you: How Do I Configure My NI Device to Be Open-Drain (Open Collector) or Push-Pull (Active Drive)?
But the short of it is that you use a pull up resistor to the 5V and wire it to the NPN output and your DAQ input.
GCentral
(3,525 Views)
Hi crossrulz,
Thanks for your answer.
Do you know what value of this pull-up resistor should I use?
Thanx.
Vanessa
(3,515 Views)
It really depends on how much current your open collector will sink.  I usually go with somewhere between 10k and 100k.  I think many of the NI DIO boards have a 47k.
GCentral
(3,504 Views)
Thank you very much crossrulz. I've connected the 5V output from the DAQ to a 9 kOhm resistor, then the sensor NPN output, and then this two to the digital signal input. It's working smoothly!
Vanessa
(3,493 Views)
