Converting modbus hex-data from one register into float
i am using the modbus-protocol to read an analog-value from a module.
The webpanel of the module displays the hex-value and the float-value. The modbus-function only returns the hex-value.
09FD is 0.780
How can i convert the returned hex-value in float?
There is also a modbus-funtion for this:
public static float GetSingle(ushort highOrderValue, ushort lowOrderValue)
But i tried all kinds of using it without luck. (It works, but it does not return the correct value)
Thanks for help
Message 1 of 18
(8,581 Views)
Part of the manual of your device should state how to convert the sent value into your decimal value.
Just a pure guess, but I would say that you likely just need to multiply by 0.0003 or something close to that.
Message 2 of 18
(8,565 Views)
Modbus devices tend to have use one of two methods to represent real numbers:
  1. Multiply them by N and write the resulting value into a register. This is what Crossrulz was suggesting.
  2. Using the standard IEEE-754 floating point representation. This is usually single precision, which requires 32 bits, so it will usually be in two registers (which is what you can see in the GetSingle function you showed). You then take the two register, join their values and cast to a SGL. Your example only appears to have a single register, so either it's incomplete or this isn't the method that's used or they use half-precision floats, which LV doesn't support. If that's the case, you might need a DLL to do the conversion.
___________________
Try to take over the world!
Message 3 of 18
(8,553 Views)
I only have one register (see attachment).
But my 4 digit hex-value can be also 32bits. I tried all kind of kombinations  but non of then created the float-values
Message 4 of 18
(8,543 Views)
What device are you using?  There has to be something in the manual about how to do the conversion.
Message 5 of 18
(8,534 Views)
It is called ET-7017 from icp-das.
Message 6 of 18
(8,531 Views)
OnlyOne,
What range is this AI set for?  +/-10V ?
Message 7 of 18
(8,515 Views)
yes,
in 10V-range i get 09FD = 0.78
in 5V-range i get 13FB = 0.78
in 1V-range i get 63EA = 0.78
Message 8 of 18
(8,511 Views)
OnlyOne,
Here a are a couple of ways to convert/scale output when range is +/-10V.
Message 9 of 18
(8,504 Views)
Perfect. Works.
Thx a lot
Message 10 of 18
(8,497 Views)
