I seriously do not know what your problem is with me but I find you extremely offensive. Do you "help" people like this with all your responses? Don't like what someone asked, keep scrolling and ignore it.

0 Kudos
Message 11 of 12
(1,211 Views)
Solution
Accepted by topic author teritask

So I did find a solution...http://forums.ni.com/t5/LabVIEW/How-to-set-OPC-Server-update-rates-with-DataSocket/td-p/62380. I had another Labview person in and he remembered the solution. Basically after setting your OPC tag, you append "?updaterate=10" where 10 is in ms.

 

Ex: .OPCTest\item1opc:\\machine\National Instruments.OPCModbus\Modbus Demo Box.4:0opc:\\machine\ National Instruments.OPCModbus\Modbus Demo Box.4:0?updaterate=100&deadband=0.7

 

So it kind of was a "hidden menu" that I was blasted for earlier...