Don,
As Khalid mentioned, first check the deadband for the i/o group and also for the tag engine. Make sure that these are small enough that you will see the change. Also, make sure that the scaling is correct for the tag. Remember: the deadbands are %'s of the scaling. So, if the scaling is incorrect, then you may not get the updates as often as you planned.
Also, try reading the tag with a read tag.vi. Lastly, make sure that the front panel connection has a green connection light and that the indicator is in a while loop while you are running the vi.
If all of these things fail, you can try reading the counter value with a different OPC Client to make sure that the server is truly opc compliant. You could use the server explorer 2.4.1 (made by Nati
onal Instruments).
Let me know if these suggestions don't help.