04-15-2016 09:36 PM
Hi All,
I need to control a temperature controller (Eurotherm 420 model) with LabView, the communication is serial communication i.e, RS422. Can anyone help me in this regard?? Is the VISA for all type of serial communication same?? I'm using the Startech USB serial cable adapter (the picture is attached here).
Thank You,
Shahab
04-15-2016 11:15 PM
VISA is the same. There is no inherent difference between using RS-232, RS-422, and RS-485 other than the adapters and the cables. LabVIEW doesn't care which is which.
04-16-2016 11:54 AM
04-17-2016 09:24 PM
I'm trying to use a eurotherm 808 temperature controller driver which is available in the following NI site. But whenever trying to communicate the controller it's showing the error "Read timeout error, no data found at serial port." Does anyone this sort of experience?? Highly appreciate your help.
Thank You,
Shahab
04-17-2016 09:28 PM
Check your serial port address, your baud rate, start/stop/parity bits. Check your cable. Check the slave address used.
04-18-2016 04:24 PM