Uwe =?iso-8859-1?Q?M=FCller?= wrote:
>Hi,>>we have a problem with our FieldPoint FP-1600. After starting it works>well.
The LEDs for LINK, RX and TX show activity.>But when we don' t use it for
a while, it seems to change to a sleep>mode. The LINK LED is on, but RX and
TX are off. In LabVIEW this causes>errors, and the FieldPoint Explorer doesn'
t work also.>The only way to awake it is a reset by switching off the power.>>Does
this sleep mode exist or is it an error?>Can we awake our device by software,
or is it possible to prevent this>sleep mode?>>Thanks, Michael>
Michael,
The FP-1600 does not have a sleep mode similiar to what you describe. You
should be able to leave a FP-1600 unaccessed for days and then immediately
link to it with no dif
ficulty (I have done this extremly frequently). Since
you are awakening the module by resetting the power supply, one theory I
can offer is that you may have a power problem or ground loop. I have seen
cases where a power supply common would drift too much with respect to the
common of other devices on the network (such as the hub) and it would be
out of range for the isolation transformer to actually convert the signals.
Additionally, National Instruments has released firmware revision 2.0 for
the ethernet modules and it offers improved performance speeds and reliability.
You may want to download it from:
ftp://ftp.ni.com/support/fieldpoint/Update/FPEthernet0200.fpf
Instructions for upgrading the firmware can be found at:
http://ae.natinst.com/operations/ae/public.nsf/fca7838c4500dc10862567a100753500/114658a35a48fd7786256890004e537c?OpenDocument
Regards,
Aaron Gelfand