Hall effect Current Sensor output

Hello everyone,

 

I am using an birdectional hall effect current sensor to measure the current in a battery cell. The output of the sensor is connected to an PLC . The sensor ouputs the measured current in the range of 4 -20mA and it can measure a maximum of 25A. i.e  4mA= -25A and 20mA= +25A. The PLC is reading the corrct value as i have checked it. when no current flows through it it shows approximatley 12mA, which  represents 0A. Now my question is, how can i programme in such a way that labview changes the measured value into actual current value in Ampere. i.e when the signal outputs 20mA, i want the labview programme to show as 25A in the front panel. Is this done using scaling and if so, can someone explain how it´s done.

 

Thanking you

Gokul Gopakumar

0 Kudos
Message 1 of 4
(1,723 Views)

Hi Gokul,

 


@Speedyindian wrote:

Now my question is, how can i programme in such a way that labview changes the measured value into actual current value in Ampere. i.e when the signal outputs 20mA, i want the labview programme to show as 25A in the front panel. Is this done using scaling and if so, can someone explain how it´s done.


So you are asking for some basic math lessons? Really?

 

You know those XY points:

 

signal  current
 mA        A
  4      -25
 12        0
 20      +25

 

And now you are looking for the calculation to convert the 4-20mA signal into the measured current (±25A)?

What about a simple linear equation:

 

current := (signal - 0.012)/0.008 * 25
or
current := 3125 * signal - 37.5

 

Best regards,
GerdW


using LV2016/2019/2021 on Win10/11+cRIO, TestStand2016/2019
0 Kudos
Message 2 of 4
(1,698 Views)

Hello Gerd,

 

Thank you for the clarification. Umm is the formula right?, because when im using it i am not getting the right values.

 

Thanking you

Gokul Gopaumar

0 Kudos
Message 3 of 4
(1,666 Views)

Hi Gokul,

 


@Speedyindian wrote:

 Umm is the formula right?, because when im using it i am not getting the right values.


I get correct values with my formulas!

Remember: your signal is in mA, so you get readings like 0.006 or 0.0195...

Best regards,
GerdW