If the PLC server supports array reads and writes you can do much better
than 30 points with DataSocket. In my experience, it is the number of
DataSocket connections you have that will slow you down rather than the
number of data points. You probably don't want more than 30 DataSocket
connections but if each connection reads or writes an array of points you
can probably get access 100s or even 1000s of points in a reasonable amount
of time. I used this method to communicate 410 registers from a total of 5
PLCs with an update rate of 5 Hz. I did have to create my own tag manager
in LabVIEW to handle the conversion between arrays and individual points.
DSC has this feature built in.