Yes Ofcourse. its different one. However I want to capture the data. Through NI OPC i got now.
I had tried same you said, before NI OPC. and I have attached also. But i didn't get the output...
12-05-2017 11:16 PM - edited 12-05-2017 11:17 PM
In your Modbus command, you are only reading 1 register.
You need to read 2 registers so that you can get two 16 bit values and be able to join them into a 32 bit value that you can typecast to Single.
Also your holding register may be #40245, but that is not the value that gets passed in the communciation protocol ad not what LabVIEW wants in the Modbus command.
Drop the 4 at the beginning. Subtract 1.
Make your Modbus command say Starting Address 244 and Quantity 2.
All you never wanted to know about Modbus.
http://www.modbus.org/tech.php