RELAY SERIAL COMMUNICATION USING ADAM 4608 MODULE
Hi all, I'm having a problem with switching of relays using ADAM module 4608. I have 4 relays with me. The vendor supplied commands to open and close relays. But while using serial communication protocol, I can only operate one relay at a time. The problem is there are four different  commands to open but only one command to close it all. I couldn't operate all the four relays simultaneously. Program I developed is attached with this message.The commands to open are, #010001,#010002,#010004,#010008 and the close command is #010000. Please go through it and help me find a solution. I'm really stuck here.
arjun
(2,685 Views)
I cna't access the tech infor for the module, but on a hunch, what happens if you issue a #010015 command?
-AK2DM
(2,639 Views)
Maybe it's hex? Try #01000F and #010003 and maybe those will put on all four and two of the relays?
Rod.
(2,624 Views)
thanks.. thats the correct solution.. 🙂
(2,614 Views)
Then mark it as a solution 😄
This will motivate volunteers and may be helpful for someone that experience the same issue as you in the future.
Best Regards
Mondoni
(2,600 Views)